Wayne
Jeff is correct in that you will need a 3-pole switch or contactor to properly disconnect your 3-phase motor. You can use a single-pole switch before your VFD, as Sleepy suggests, if you are using a single-phase 110V input to your VFD. If you are you are using a 220V single-phase input to your VFD, then both connections are actually hot so you would need a 2-pole switch to properly disconnect your VFD. Depending on the VFD that you are using, the current drawn by the VFD might blow up a normal "light switch" that you would get from Home Depot so you may want something beefier.
I do not recommend relying on an on-off fuction controlled by your VFD. If a fault occurs in your VFD, you may not be able to turn off the power to your motor. For safety, you NEED some way to totally disconnect the power to your VFD that is located near your VFD. You don't want to have to run back to your breaker panel to shut of the power in an emergency.
If you are using 220V to feed your VFD, I can send you a USED 3-phase contactor if you reimburse me for the postage. The main contacts are rated at 600Vac, 35A continuous. The coil is 220V/240V. It is about a 4 inch cube. The terminals are exposed so you will have to mount it some kind of box. You can mount the switch to control the contactor on the front. Please remember that it would be a USED item with uncertain history. I can check it for function before sending it but no guarantees or warranties. The service department here at Toshiba just scrapped a whole bunch of older electrical equipment, mainly UPS', so their scrap bins are overflowing with stuff like this. Send me an e-mail if you want me to grab one for you.
Phil