I know this may not be the best place to ask this question, but I figure some one here might know and it's knife related....so:
My grinder motor is currently wired directly into a 30 amp disconnect that I use as a switch per the direction of the electrician that hooked it up for me. It works great with no complaints.
However, with the delivery of a 220 volt kiln, I want to add an outlet in this set up so I don't have to run another 220 volt circuit.
The kiln that's coming uses a NEMA 6-20P, 20 amp plug.
The grinder is currently wired directly into the disconnect which is mounted on the wall. The wire is some 3/8" diameter black stuff that's rated to be left exposed with no conduit....I'll look for the type of the wire tonight when I get home if that matters.
The circuit is 30 amps....obvious given the disconnect, but making sure the info is out there for review.
Question is this....can I cut the wire run between the grinder motor and the disconnect and put a Nema 6-20P outlet on the wire coming out of the disconnect and a Nema 6-20P plug on the wire coming out the grinder? This way I can use the one outlet for either the kiln or the grinder motor.
I'm assuming I can. The grinder motor is rated at 9.5 FLA at 220 volts and the kiln at 11 amps, so my assumption is that if the 6-20P plug will work for the kiln, so will it work on the motor.
Assumptions correct? Anything I'm missing?
My grinder motor is currently wired directly into a 30 amp disconnect that I use as a switch per the direction of the electrician that hooked it up for me. It works great with no complaints.
However, with the delivery of a 220 volt kiln, I want to add an outlet in this set up so I don't have to run another 220 volt circuit.
The kiln that's coming uses a NEMA 6-20P, 20 amp plug.
The grinder is currently wired directly into the disconnect which is mounted on the wall. The wire is some 3/8" diameter black stuff that's rated to be left exposed with no conduit....I'll look for the type of the wire tonight when I get home if that matters.
The circuit is 30 amps....obvious given the disconnect, but making sure the info is out there for review.
Question is this....can I cut the wire run between the grinder motor and the disconnect and put a Nema 6-20P outlet on the wire coming out of the disconnect and a Nema 6-20P plug on the wire coming out the grinder? This way I can use the one outlet for either the kiln or the grinder motor.
I'm assuming I can. The grinder motor is rated at 9.5 FLA at 220 volts and the kiln at 11 amps, so my assumption is that if the 6-20P plug will work for the kiln, so will it work on the motor.
Assumptions correct? Anything I'm missing?