zaph1, 5 true hp cant be pulled from a 110v outlet..Thats over 33 amps, 3730 watts of power..Way more than a standard 110v outlet was designed to handle..
.
Ive done a lot of research and talking to knowledgable folks since I started this thread..Theres a motor shop less than a mile from my house..
Im not a electrician but the math is correct..You'll get no more than 1875 watts from 15 amps at 125 volts...
Even if the motors energy efficancy was 100% (which it aint) Your still only looking at an available 2.5 hp from a 15A, 125v breaker and thats if it was giving 100% without tripping which it would on the startup phase..On a 20A breaker at 125v your looking at a max of 3.3 hp at 100% motor efficancy and without the breaker tripping..
.
I think that some newer motors are rated on "peak" power, not continuous. It takes "x" ammount of amps to get "x" ammount of watts to matter what you do.No motor can do otherwise.Volts*Amps=Watts, Watts/Volts=Amps
Heres a formula I found..
voltage x amps x efficancy
hp=----------------------------
746
Meaning if you have a motor that has a 70% efficancy rating, uses 125v and draws 9 maps its hp would be 1.0 hp..
.
Baldor uses the formula voltage x amps x efficancy x power factor= output watts..baldor does list thier efficancy and power factor on the nameplate, or they did anyway..
heres a link I found about air compressor motor ratings...
http://www.asedeals.com/air_compressor_faq.pdf
.
Most every website I found uses a loose guideline of 10 amps per HP on 115v and 5 amps per hp on 220v..