Motors can get very confusing in a hurry.
Formally, motors require 2 types of protection:
1. short circuit
2. thermal overload
Because the normal start-up current can be very high, the fuses/ circuit breakers used to protect the wiring need to be over sized to reduce a nuisance fault from starting the motor. Since the fuse/cb is oversized, the motor is unprotected from prolonged over current. The motor will heat up and could be damaged. This is where the thermal protection comes in. This is slow tripping feature that needs to trip at lower current levels but requires an extended time before it activates so that it doesn't prematurely kick-out during start-up. Not good for short circuit protection since it takes time to activate.
The Leeson 2hp motor has a name plate rating of 9.2A @ 220V. This is the full load amperage....not the start up amps. The actual "starting-amps" will vary based on the machine and how inertial load needs to get moving. A motor without anything mounted on the shaft will start will less current than a motor with a flywheel on the shaft. With this in mind, it is difficult to predict the starting current. For a belt grinder....no issue.
Anyway, there are some fuses specifically designed to offer both types of protection for motors. They have dual elements, 1 for short circuit, and the other for thermal over load. When they blow, they have different indicators based on the type of failure.
As far as the Leeson 2Hp and your grinder goes......your in luck! That particular motor has thermal protection built in. It is a manual reset button on the front of the connection box. So all you need to do is wire the motor with conductors rated for 30 amps (circuit breaker size) and your set. From there the motor will protect itself. Plug it in and start grinding!.....I love these Leeson motors!
Good luck,
Rob