I'm an electrician (going on 20 years) and have never used a Chris Reeve knife at all. I have handled them. If anyone wants to send me one I will gladly use it. Just PM me.
Hmmm.....don't let the inspector see that. Just a few code violations.If I felt you were going to burn your house down I'd list them, but looks safe enough.
Thanks for your assistance, my answers in blue above :thumbup:Cereal_killer,
A couple things id look into are.
1. You should put some kind of connector on the wires entering the panel. A kid or animal or something could snag them and pull them enough to cause problems.
this is gonna sound really bad but what do you mean by connector? Can you link me to an example?
2. Since you are feeding this from another panel. You should seperate the equipment grounds and neutral wires. By putting them together you are essentially paralleling the nuetral and not getting a seperate path back to the source (main panel)
In the event that you get a ground fault on the main cord you could potentially not get that feeder breaker to trip fast enough and cause the cord to over heat and start a fire.
so should I add in another bar? What's the best way to do this? All of the outlets on this aux panel are GFCI, does this mean they won't work?
3. You have 3 different brands of breakers in the box which looks to be a square d hom box. The one in the middle concerns me I have no idea what kind that is. The siemens double 30 is okay as they stab on the same as a hom I wouldnt worry too much about that one.
self explanatory, I'll get on it today
Also what size breaker are you feeding the sub panel with? That looks like 10/4 cord which if im not mistaken is only rated for 25 amps with 3 current carrying conductors. And if you are running it for a long distance id be concerned about voltage drop when running your 20 amp 240v load.
the feed beaker 40A, wire is 8-4 with all 4 wires insulated, is this sufficient? Also the main panel is only a few feet away, the cable is 6' between them.
Keep it safe out there.
Thanks for your assistance, my answers in blue above :thumbup: