Techinically the 8/4 SO Cord is only rated at 35A being there are 3 current carrying conductors in the cable, but I think it should be fine being temporary and at a short distance. You should be okay with that.
Also is your welder a 120/240v or straight 240, if it's straight 240 you should move the ground wire to your newly installed ground bar.
And I should have mentioned if this before but, if you haven't worked with connectors before, you don't have to crank them all the way down til the screws won't budge, just tighten them enough so the cable will not move if you tug on it. Might be self explanatory but you never know.
I don't know that this information is accurate. I also haven't bought 2014 code book yet. I did just complete a code change class and there was no mention of changes to the ampacities table.Looking much better C_K.
Techinically the 8/4 SO Cord is only rated at 35A being there are 3 current carrying conductors in the cable, but I think it should be fine being temporary and at a short distance. You should be okay with that.
Also is your welder a 120/240v or straight 240, if it's straight 240 you should move the ground wire to your newly installed ground bar.
And I should have mentioned if this before but, if you haven't worked with connectors before, you don't have to crank them all the way down til the screws won't budge, just tighten them enough so the cable will not move if you tug on it. Might be self explanatory but you never know.
You have to jump over to Article 400 "Flexible cords and cables" and then use Table 400.5(A) for So cable, Can't use table 310.16 (2011 nec) or 310.15(B)(16) since there is no SO or SJO or SOOW in the table.
Looking at Table 400.5 going to a 8 AWG and over to column "A" since there are 3 current carrying conductors (Column B is for 2 ccc) shows 35 Amps.
Article 240.4(b) allows you to use the next size higher standard overcurrent device, but since a 35 Amp breaker exists you are required to put it on a 35amp breaker.
Also a 40 amp breaker should hold 39 amps for exteneded periods of time, (you would have to look at the manufactures time/current curve) but in the nec you are allowed to load a circuit breaker to 80% of it's rating which is 32 amps.