Geek alert: EE trying to clear an electrical misconception!
Hopefully this link will take you to a chart for the time/current trip curve for a typical GE circuit breaker used today for residential panels. It is your standard 'snap in' type breaker found in panels and home improvement stores everywhere, but the idea is typical for all standard CB's. When I cut&paste it into my browser it works...
http://www.geindustrial.com/publibrary/checkout/Time%20Current%20Curves|GES-6202A|generic
Note that the top/bottom scale is rated in
multiples of the rating. For example, at 2x, the acceptable time to "clear" (the term for tripping the breaker, technically 'clearing the fault') a 2x overload is 15-100 seconds. At 10x (that is 500 amps in our 50 amp example) the range is 0.3-2.0 seconds. I have the formula at my desk at work to calculate short circuit current based on wire size, transformer capacity, etc. and I could throw out all kinds of numbers...but I'll just say that 500 amps for even 0.3 seconds will fry a lot of 14 AWG wire. Due to typical QC practices the normal response is probably near the middle of the curve. Anyone who has experienced a hard short will recall that it hummed/buzzed for an instant or two before the breaker trips...this is why. The breakers are made to do that...hence the term "time delay breaker".
This time delay is eliminated in a GFCI breaker, and that plus the fact that they actively clear in milliseconds and they clear on a 25 milliamps of short circuit current should clearly illustrate why they save lives...