Stacy is right. The VFD's are designed to have unimpeded airflow to keep them cool. Putting them in a sealed box requires a heat exchanger mechanism. They do this here for certain special applications that can bear the extra cost of the heat exchanger.
The cause of the other forum member's VFD blowwing up was likely to be the metal dust being moved around to the "wrong place" when he was vacuuming the dust, with the input power turned on. The lesson here is that if you must blow/suck the dust out of your VFD, make sure that the power is off before you start.
Rocketmann
Look on page 11 and 13 of the "Maintenance Manual" to see how to connect the input mains power and your motor. It can be downloaded from
www.twmi.com/products/controls/drives/FM100. I suspect that you have a 220 V, single-phase supply so you will be using the L1 and L2 terminals. The motor wires would connect to the T1, T2 and T3 terminals. The motor wires are likely to be marked T1, T2, T3 or U,V,W as shown on page 11. Don't worry about the "Thermal Relay" and "Thermal Overload Relay" shown on page 11. They are really only used on much larger (more expensive) motors and VFD combinations. If your motor ends up turning the wrong way, swap two of the motor wires. According to the National Electrical Code, you should use at least least 14 AWG wire for the power and motor connections if you have a 2 hp VFD. Use at least 12 AWG wire if you have a 3 hp VFD.
Go to pages 11 and 28 to see how to connect the remote speed setting potentiometer. Use the connection scheme shown at the far left and program Fn_11 to the value described. If you are willing to spend up to $25 get a 10-turn potentiometer (3590S-2-103-ND) and a matching turn-counting knob (H-550-6A-1-ND). It will give you very fine control of your speed. A less expensive option is a single turn potentiometer (RV4N103C-ND) and a normal knob (8556K-ND) at about $11 - $12. I have given the Digikey (
www.digikey.com) catalogue numbers for each item. All of these parts are of good quality from reputable manufacturers that I would have no trouble using in the equipment that I design.
Go to page 24 to see the various options for the ON/OFF switch by your grinder. If you need to be able to reverse the direction of the grinder, use the middle connection scheme. If you only need the forward direction, then use the lower connection scheme but omit the switch for "Reverse". Of course, you will have to program the values for Fn_10 and Fn_03 as shown in the manual. I would recommend the Z1502-ND from Digikey at $28.58. It is sealed against dust and water and has a big, red "mushroom" that a quick slap of the hand will stop the power to the motor in an emergency. Keep in mind that the VFD is still live and that your dryer plug is still your "power switch". You could install a 220 V, double pole breaker between the power cord and the VFD to act as a switch and give you some protection in case something bad happens inside your VFD. If you have the 2 hp VFD, use a 15 A breaker. If you have the 3 hp VFD, use a 30 A breaker. These sizes should make you "legal" with the NEC.
The wires used for connecting the switch and remote potentiometer can be anything from 20 AWG and up since the current is very small. A piece of network cable would work. A plastic dual-gang electrical box with a blank plate from Home Depot would be a good choice to mount the switch and potentiometer on.
If possible, have a qualified electrician confirm the wire size and circuit breaker sizes and check your wiring.
Sorry for the long post. Hope this helps.
Phil