Is anyone running a VFD on their grinder (running on a 110 circuit with 2 hp motor)?

Joined
Dec 1, 2010
Messages
10
Is anyone running a VFD on their grinder (running on a 110 circuit with 2 hp motor)?

I just have a quick question.

I have a 2 hp motor but if you hook it up to 110v, it only runs at 1.5 hp... So do I set the VDR to 2 hp or 1.5 hp?

Thanks in advance


qlG6a
 
Last edited by a moderator:
On mine, If the drive specifies 1.5hp max on 110v, it's set to 1.5.


Sent from my iPhone using Tapatalk
 
Typo... I meant VFD

This is a KBAC 27D from KB-Electronics.

My outlet is 110v... The motor is a 2 hp Leeson.

One would think type set the VFD up for 2 hp... but since it's a 110 line, 1.5 hp is what the motor will run at... So do I set the jumper to 1.5 or 2.0 hp! I don't want to damage anything.
 
Typo... I meant VFD

This is a KBAC 27D from KB-Electronics.

My outlet is 110v... The motor is a 2 hp Leeson.

One would think type set the VFD up for 2 hp... but since it's a 110 line, 1.5 hp is what the motor will run at... So do I set the jumper to 1.5 or 2.0 hp! I don't want to damage anything.

1.5

And the 110/220 jumper at 110
 