Kiln re-wiring help!

Here are the settings..

Inty. Backward 4 for k type thermocouple

Outy. 2

Atdu. 0 (this was in place of " hy" setting)

Psb. 0

Rd. 0(for heating)

C or f. 1 (for degrees f)






P. 5
I. 100
D. 20
Souf. .2
ot. 2
Filt. 0

The next settings I entered for the simulation during subroutine..not sure if it's right I used the scenario in the back of manual, which wasn't all that easy to understand. Thanks for your advice.
 
Luke says he's tried the various tests suggested and found low voltage coming from the SSR. He hears a click from the relay but it doesn't heat. His theory is wrong settings,, which is why he posted them above.

Anyone able to diagnose from afar?
 
I just had a thought when reading your "click" comment - Are you positive you have the right PID? They can be ordered in relay output control ( usually designated with an "R" in the model code) or with SSR output control (Code S). If you connect a relay type PID to an SSR with no DC power in the circuit, nothing will happen when the relay "clicks". I see that the one you linked to is dual output, but there is a possibility that it is wrong, or the SSR out isn't working. Double check that the program is set for SSR out, and that there is voltage coming from the SSR +/- terminals. See last paragraph for how to fix that. Some PIDs have to be programmed for either R or S control. Make sure you are in the SSR mode if that applies.




Earlier thoughts:

Are the wires from the PID to the SSR connected to the "NO relay" terminals or the SSR +/- contacts? The SSR needs 3-230VDC to operate. This applies to PID units with both SSR and relay output.

Did you do the test where you apply a DC voltage to the SSR? That test will tell you if the coils power circuit is right. If applying DC directly to the SSR from an outside source causes the coils to heat, the problem is either that the PID is wired wrong to the SSR, or the PID isn't working right.

Here is how I would troubleshoot this problem:
1) Temporarily put the power wires that are on SSR terminals 1 and 2 on the same terminal (say, both on #1). This should make the coils heat up when you flip on the main power switch. If the coils don't heat up, there is a problem with the coils wiring. If the coils heat up, proceed to next test.

2) Put the power wires back on SSR#1&#2 as normal. Apply 12VDC to the SSR terminals #3&#4, observing polarity. Switch on the main power switch. The coils should heat up. If they don't heat up, the SSR is bad. If they heat up, proceed to next test.

3) Check the SSR +/- voltage from the PID while it is in the RUN mode. There should be 9-12VDC on the two terminals. If no voltage is found, either the PID is bad, the PID is not an SSR type ( or programed for SSR), or the PID isn't in the RUN mode.




If you are pretty sure that the PID is trying to turn the SSR on and off (relay clicks), but there is no power from the SSR +/- terminals, try this:
Use the DC source you tested the SSR with in the above tests and connect the + to the SSR ( should be + terminal #3), the - to one of the PID relay NO contacts, and a wire from the other PID relay NO contact to SSR - terminal ( Should be - terminal #4). With this configuration, you are running the SSR on the relay out circuit, not the voltage out circuit. If it runs the coils this way, the PID has a problem with its DC out circuit, but you can run it on the relay circuit just fine.
 
Last edited:
Well, after much fumbling about and burning out a few SSRs, I finally got it to heat up without going kablooey. Initially it was heating at a rate of about 3 seconds per degree Fahrenheit. All well and good, right?

Except that it slowed down to about 9 seconds per degree, and then finally stopped at around 1070 degrees. I have it programmed at 1525 degrees. It just sat there and went up and down a few degrees, but no hotter than 1075.

I feel like we're on the verge of getting it right, but we aren't there. I need to get this working and get a-rollin' on orders that are waiting on it. If I can't get this working in the next couple of days, I'm probably going to break down and spend the money on a commercial kiln. More important than the money, though, is the time as it will be 3 or 4 weeks before the kiln ships. Which means lost money, of course.

Anyone have any ideas on what I should try next before throwing in the towel?
 
If it is heating that slow you either have to small of elements or you are not turning them on or turning them on with too low of voltage. If you put a 110 leg across a 220 element you will only get 1/4 the wattage.

The voltage output from a strraight SSR should be what ever it is supplied.
 