In your drawing of the frame you made to place the knife in, the steel looks pretty thick. If it has too much thermal mass, the delay time in heating control will make it hard for the PID to figure out how long to fire the heating elements.
1/8" plates are more than thick enough. They mainly are there to block direct radiation from the elements. You need to leave plenty of room for the air to have convection, too. don't completely cover the shelves with metal plates.
BTW, make sure the oven is set to run on HIGH, BAKE., and the temperature dial (if there is one) is at its highest setting. (Or, re-wire the oven to by-pass the controls so elements to run directly off the power cord if that is possible.)
MRCHIPS said:Either the PID controller is busted or it needs tuning.
Disable auto-tuning.
Disable both integral and derivative control by setting the Integral Time and Derivative Time to max (3600 seconds).
Experiment with Proportional control first. P controls the power, i.e. how fast you want to ramp up the temperature. You ought to get some reasonable form of control even if there is deviation from the setpoint.
Start reducing the Integral Time. Integral control is to reduce the error from your setpoint. This ought to correct the error from the setpoint. For temperature control, many times PI control is good enough. Adjust P and I to get best settling time without too much oscillation. Only after the P and I controls are working should you attempt to introduce D control.
The purpose of Derivative control is to take care of short term perturbations. It will also help to reduce oscillations.
I'm having some difficulty understanding the intent behind your setup. The "conceptual" drawing actually looked pretty sound to me. The photo looks nothing like it. At all.
The drawing shows a thick bottom plate, which might reasonably be expected to work as a heatsink, with the thermocouple embedded in it. The plate is shown as being heated by radiated heat from the lower elements. There is a similar top plate which might reasonably be assumed to be heated by radiation from the top elements, and to a degree reasonably similar to the (measured) bottom plate. The blade is shown standing vertically in a rack between the top and bottom plates.
The photo seems to show foil on the shelf so that the bottom plate is not heated directly by radiation from the bottom elements. The control thermocouple is placed above the bottom plate, not within it. It looks like it may even be on top of the second thermocouple. There are no support pillars visible for the top plate. Is there even a top plate? Without one, the primary heating mechanism would seem to be radiated heat from the top elements. The blade is positioned flat on the bottom plate. It is notable that both thermocouples look shiny. This is not generally a good thing when trying to measure/control a process involving radiative heating.
Why have you made such major changes between the concept and testing stages? Did you even realise that you had made changes? Do you realise now that it has been pointed out?
Although I suspect that the controller is not a particularly good one, I am inclined to feel that several aspects of your process setup are contributing to the problem.
I'd suggest you order a new controller and build/test the setup in the drawing while you are waiting for it to arrive.
I just though of something the advice from timgunn made me think of. It may not be your issue, but is worth mentioning.
The rate of many lower cost ramp/soak PIDs is the opposite of some others . rate9999 is 9999° degrees per hour ramp rate on some PIDs. StepTime9999 ramp rate is 9999 minutes to the next step on others. Make sure which your program manual calls for. Also, make sure your oven will ramp in the time allotted.
I have to watch for this between my HT oven where rate5000 is a good ramp rate, and a plug in type controller I put on an old smaller oven (like what you are building), where the rate of steptime15 is about right.