too good to be true grinder quit

Technical Features: Input & Output​

Input Voltage : 220V, single phase or three phase
Do you have to set that as a paramater ?
 

Technical Features: Input & Output​

Input Voltage : 220V, single phase or three phase
Do you have to set that as a paramater ?
yes ,all parameters are set correctly,now there is a code "ELun" Drew walked me through checking the motor which checks out with my basic meter, so I've ordered a new vfd which will hopefully arrive later today.
 
new vfd arrived, the fan turns on when powered up the original didn't. here is what I programmed for settings don't want to turn the motor on until I have confirmation my numbers are ok
( will dispense the "Pd")
3, 4, 5 are at 60hz
9 is 14
10 is 7
14 is 20
141 is 220v
142 is 5.5(amps @ 220 on motor )
143 is 2
144 is 3450 ( as per motor plate)
 
I don't think you want your Accel. time (Pd014) to take 20 seconds to ramp up. I'd drop that down to no more than 4 or 5 seconds. 1 or 2 would even be fine.

Other than that, I'd say those parameters should be just fine. Assuming you wired it just like the last one, you can set for external controls, hit the switch, and see what happens.
 