Hi Rashid11,If using a typical PID controller and an SSR (a solid state relay, as opposed to the electro-mechanical variety), w/o powering anything up just yet:
1) wire power wires to PID controller. Most use _any_ voltage, including 120V or 240V AC.
Some (very few) require dedicated 12V. Check your model
2) run 2 wires from your K-type-thermocouple to the TC input of your pid controller
3) run 2 SSR control wires from the PID controller to your SSR control input (2 terminals)
4) wire one leg of the spiral to the neutral leg of power circuit if using 120V or any of the 2 hot legs if using 240V
5) wire other leg of the power circuit to one of of the 2 power leads on the SSR
6) connect other end of the spiral to the second (remaining) power lead on the SSR
7) make sure to ground the exterior of the oven
Now turn on the power to the SSR. You'd need to run initial setup: set F or C, tell it you have an SSR, tell it you're using K-type thermocouple. Ideally, run a training cycle - it will learn the thermal dynamics of your oven. Follow your manual
ib2v4u, Ah thanks,It is a switch to kill the legs of 220 power to the PID and ssr. It takes the 220 inputs and and shuts them off and on. I did this. I also added a push button sw to one of the wires to the relay coil ( I actually used a SSR) Then set it up so when I opened the door it killed the power to the elements. You could do it with a simple spst toggle also. If you hit a blade to a live element you might not like it.
Btw do you mean you have the wires from the thermocouple to terminal #1 and #2?