I did look in where the brush goes with a flashlight and it looks bright and shinny .That brush really doesn't look bad at all. Could be some corrosion on the comm? I'm still leaning towards a possible cap issue.
The BladeForums.com 2024 Traditional Knife is available! Price is $250 ea (shipped within CONUS).
Order here: https://www.bladeforums.com/help/2024-traditional/
I did look in where the brush goes with a flashlight and it looks bright and shinny .That brush really doesn't look bad at all. Could be some corrosion on the comm? I'm still leaning towards a possible cap issue.
Sounds like the brushes aren't the problem.I did look in where the brush goes with a flashlight and it looks bright and shinny .
I just recently put a power "on-off" switch on the Baldor DC drive on the Bader III in the shop. The motor control company I ordered the part from sold me a KB drives part, and told me that KB makes the drives for Baldor. Might be worth a call to KB technical support to see if they can help with the problem?
No, it's a DC motor, it needs the controller to run.Thank you for your input . I sure hope it's not the Baldor drive but if it is I will have to deal with it. I guess if I bypassed the controller and hooked the motor up direct and it ran full speed that would pretty much point to the controller .?
OOPS ! Showing more of my ignorance . ThanksNo, it's a DC motor, it needs the controller to run.
DC motors are voltage controlled, not frequency controlled.
What makes me suspect the issue is in the controller is that Baldor controller is 120 or 240 volt AC input. It converts that to 180VDC. If the supply is 120 volts and the jumper has been moved/disconnected, or a component failure has switched things to 240VAC input mode, the unit may be putting out 90VDC. That will run it as normal .... but the max speed will be half what it would be on 180VDC output ... which is the issue you are having.
If you are running the unit on 220VAC, another reason this would happen is if one leg is dead. It could be running on only one leg and ground.... which would be 120VAC.
Check the breakers and have someone check that there is 220VAC at the socket. I'm not sure this applies to taat controller, but it is one of the first things to check.
If the socket and breakers are fine, there are two small Buss fuses in the controller (15amp IIRC). Unplug the unit and check/change both, then try it again.
120 volts to ground on both incoming hot legs is good, but you need to test leg-to-leg and see if you have 220-240 volts AC or so. For the output test, you would test across the 2 wires going to the motor that are not the ground (green)
So you put both leads from your tester , one one each hot line ? Nothing to ground ?
Sounds like dropping the tester was a good thing. I don't think you understand electricity and electric circuits.
The output is DC, so it is read on the meter's DC scale and is polarity sensitive. Your motor should be receiving 180VDC. That would be read across the two wires.